Dear Sir, These are the points to be discussed before doing any change of your

Ahmed

New member
building. Since the First? Dear Sir,


These are the points to be discussed before doing any change of your building. Since the First Floor ceiling Slab are already concrete few months ago and contractor done the electrical and mechanical works as per the following:
1.A/C copper pipes for ground floor, mezzanine floor are traveling from the beam it has to be change the direction.
2.A/c power conduits from each DB passing through the walls to roof for all floor has to be change, to do so it requires extra wiring ,GI conducting ,additional cable tray etc.
3.DEWA will not allow using multi meter in single Zone, as per the approved drawing we have 4 meter in four offices it has to revise and re submit for the DEWA approval and which is time taking.
4.Electrical power layout drawing has to be change and resubmit for DEWA approval.
5.AC thermostat location should change and the location to discuss.
6All power sockets which are coming on the wall has to change and location to be discuss.
7Location for the fire hose real cabinet has to be change and location has to be discuss again and drawing to be revised.
8Architecture drawing has to be change and has to take the approval from DM as per new layout.
9Fistula approved drawing has to be revised.

Due to the above following, much additional work has to be done and addition of materials in mechanical and electrical (piping, cable tray, conduits, cables and wires, trucking and floor boxes, supports and accessories), may requires. These may lead to time consuming and cost increasing in the completion of project.
 